• 22.9 kV-y, three-phase single-phase pole transformer for multi-grounding distribution system
• Highly efficient transformer with minimum load loss
• Radiator-free transformer with reduction of load loss and no-load loss, little noise, wide high-temperature range and slim physical structure
• High-efficiency transformers (in energy consumption efficiency)
– Reduction of load loss and no-load loss
– Little noise
– Increase in overload and harmonic wave withstand
• Less surface needed for installation and slim pole use available
(100 kVA or below)
• Environmentally-friendly with the use of natural ester oil
• Capacity : 20, 30, 50, 75, 100 kVA (mineral oil & natural ester oil)
• Frequency : 60 Hz or upon client's requirement
• Primary voltage : 13.2 kV
• Secondary voltage : 230 v or upon client's requirement
• Tap voltage : 3 taps
Single-phase(1Φ) 13200V / 22900GrdY - 230V, 60Hz
Capacity (kVA) |
Efficiency (%) |
Voltage regulation (%) |
No-load current (%) |
No-load loss (W) |
Load loss (W) 100% load |
|
Load factor 50% |
Load factor 100% |
|||||
20 |
98.61 or above |
98.61 or above |
1.7 |
1.0 |
48 |
232 or below |
30 |
98.71 or above |
98.71 or above |
1.5 |
1.0 |
62 |
327 or below |
50 |
98.83 or above |
98.83 or above |
1.4 |
0.8 |
89 |
501 or below |
75 |
98.92 or above |
98.92 or above |
1.4 |
0.8 |
132 |
681 or below |
100 |
98.99 or above |
98.99 or above |
1.3 |
0.7 |
165 |
851 or below |
- KEPCO standard applied
- Specifications customizable upon client's request
Capacity (kVA) |
Dimension (mm) |
Weight (kg) |
|
||
W |
D |
H | |||
20 | 470 |
600 |
1,120 |
195 |
|
30 |
480 |
610 |
1,160 |
225 |
|
50 |
520 |
660 |
1,210 |
300 |
|
75 |
560 |
720 |
1,240 |
375 |
|
100 |
570 |
730 |
1,260 |
435 |
- Manufacturing tolerance: ±5 %
|
|